Data table showing impedance of various EGC's

Status
Not open for further replies.

bbaumer

Senior Member
Location
Indiana
Some years ago I saw a study that proved that rigid aluminum conduit was the most effective equipment grounding conductor through impedance measurement, skin effect and fault current carrying ability testing.

I'm pretty certain it also proved GRC, IMC and even EMT - when properly installed - to all be superior to a "skinny" copper conductor sized per then 250.95, now 250.122 for "typical" pipe and wire sizes for branch circuits and feeders. I don't recall now if EMT data included different fitting types or if they just used steel compression or steel set-screw or die-cast etc.

I may be wrong about the various steel pipes vs. copper wire but am certain that rigid aluminum was the best. I think the study went so far as to mention any loose couplings in steel raceways being welded together under a fault but I also may be wrong about that.

Is anyone familiar with such a study and if so know where to find it on the net?
 
Last edited:
i seem to remember that too. It was long ago so it would have been at either Tom Henry's or Joe Tedesco's site (sorry Mike) We had the opportunity here to do some DC current testing at a local testing lab years ago. We were doing an install of a 600volt 3000 amp DC power supply and the engineer in charge wanted to show us some neat things they were working on. If memory serves me 1/2 EMT would handle 1200 amps before it failed
 