Take the hot and neutral wire nut them together, that is a 'bolted fault'.


It is a fault that is so well connected that there is very low resistance, there will be no arcs. etc.
 
i was mistaken i just googled it. a bolted fault is when the conductors are actually touching heres a picture i found that might help
cse0711codes01.gif
 
Bolted Fault

Bolted Fault

You can have a three phase 'bolted fault', or other types. I take this to mean that there is no impedance to ground.

~Matt
 
Consider a 'bolted fault' to be a short circuit with a conductivity equal to the conductors in question.
 
Dave Dungan said:
Could someone explain to me what is meant by the term "bolted fault"?
I would assume the term means mechanically connected as in bolted bussbar or terminated to a contactor motor leads like in the demonstrations of bolted fault that I have watched in training classes. As opposed to an arcing fault of 2 wires making contact much like a welding stinger and causing an ionization and conductivity of surrounding atmospheric air causing a conductive plasma cloud. Much more destructive due to the plasma cloud of molten metal and conductive ionized gasses.
 
quogueelectric said:
I would assume the term means mechanically connected as in bolted bussbar or terminated to a contactor motor leads like in the demonstrations of bolted fault that I have watched in training classes. As opposed to an arcing fault of 2 wires making contact much like a welding stinger and causing an ionization and conductivity of surrounding atmospheric air causing a conductive plasma cloud. Much more destructive due to the plasma cloud of molten metal and conductive ionized gasses.

Thats pretty good, did you just make that up?
 