Using this Dayton 2NNR7 Thermostat to control 240v fan forced heater unit (2000W).
Pictures show thermostat to be used and instructions for its wiring.
I basically understand how it needs to be wired but just would like confirmation as I have not wired one of these before.
Here is the link to the manual. I believe Figure 4 would be the way to go. Simple fan forced hot air heating unit; residential size being used in a laundry room common area for tenants to do wash. Two hots to thermostat. One hot wire nutted together and back out to heating unit and the other hot incoming to "R" and then back out to heating unit on "B" and ground the thermostat. Using 12/2 and 20amp 2 pole breaker, so far as we do not have the actual heating unit where the name plate may dictate otherwise. Would have preferred to use a two pole thermostat but this would work.
View attachment 13626View attachment 13629
Pictures show thermostat to be used and instructions for its wiring.
I basically understand how it needs to be wired but just would like confirmation as I have not wired one of these before.
Here is the link to the manual. I believe Figure 4 would be the way to go. Simple fan forced hot air heating unit; residential size being used in a laundry room common area for tenants to do wash. Two hots to thermostat. One hot wire nutted together and back out to heating unit and the other hot incoming to "R" and then back out to heating unit on "B" and ground the thermostat. Using 12/2 and 20amp 2 pole breaker, so far as we do not have the actual heating unit where the name plate may dictate otherwise. Would have preferred to use a two pole thermostat but this would work.
View attachment 13626View attachment 13629