We are setting up lab facilities for testing power supplies and ruggedized equipment that are used in aviation, ground vehicles, and ships. (military applications) This equipment runs on a variety of power including 28 VDC, 120/208y 3-phase 400 Hz, in addition to 120V 60 Hz. Our 28 volts and 400 Hz comes from converters. All three power systems need to be routed through filters into an EMI test chamber. I am looking at the chamber's interior wiring and need to select receptacles that will allow connection to appropriate power. For the 120 volt that is standard straight blade. For the 120/208 400 Hz I figured on using a 20A twist lock NEMA type. Now for the 28V, the supply will operate up to 35 Amps so I was considering using a 30A twist lock type but don't know if NEC allows DC power on a NEMA style receptacle. Some of the Non-NEMA types carry a DC rating. I figured Non-NEMA couldn't be used in new work?
Can I use a standard NEMA locking receptacle provided no other receptacle in the facility uses that style for another voltage? If not, what about the Hubbell Variload receptacles? They have unique center pins for different voltage use. Anybody here installed these?