Doug248
New member
- Philadelphia suburbs
I am working on a preliminary design for a solar facility in Pennsylvania, USA. The construction manager would like to utilize a single trench to route all AC and DC cables. Some issues have come up that may or may not be code related. I appreciate any suggestions or comments.
1. AC and DC will run in separate conduits within the trench. However, when the conduits enter a quazite handhole/junction box, does AC and DC need to have a physical barrier within that box? If so, is it typical to have a barrier down the center? Conduits come in/out on all sides.
2. As far as I can tell, there is no minimum separation required between AC and DC cables, according to the NEC. Is that correct?
3. The DC cables are running at +380V and -380V. I was told that this means the phase-to-phase voltage is exceeded if using 600V cable. This generally makes sense, but I think it would be fine using 600V cable. I was also told this violates the "low voltage directive", but I believe that only applies to European countries.
4. On another note, does anyone know of a good training program for solar facility design?
Again, thank you for your time.