DC and AC trench system

Status
Not open for further replies.

Doug248

New member
I am working on a preliminary design for a solar facility in Pennsylvania, USA. The construction manager would like to utilize a single trench to route all AC and DC cables. Some issues have come up that may or may not be code related. I appreciate any suggestions or comments.

1. AC and DC will run in separate conduits within the trench. However, when the conduits enter a quazite handhole/junction box, does AC and DC need to have a physical barrier within that box? If so, is it typical to have a barrier down the center? Conduits come in/out on all sides.

2. As far as I can tell, there is no minimum separation required between AC and DC cables, according to the NEC. Is that correct?

3. The DC cables are running at +380V and -380V. I was told that this means the phase-to-phase voltage is exceeded if using 600V cable. This generally makes sense, but I think it would be fine using 600V cable. I was also told this violates the "low voltage directive", but I believe that only applies to European countries.

4. On another note, does anyone know of a good training program for solar facility design?

Again, thank you for your time.
 
I am working on a preliminary design for a solar facility in Pennsylvania, USA. The construction manager would like to utilize a single trench to route all AC and DC cables. Some issues have come up that may or may not be code related. I appreciate any suggestions or comments.

1. AC and DC will run in separate conduits within the trench. However, when the conduits enter a quazite handhole/junction box, does AC and DC need to have a physical barrier within that box? If so, is it typical to have a barrier down the center? Conduits come in/out on all sides.

2. As far as I can tell, there is no minimum separation required between AC and DC cables, according to the NEC. Is that correct?

3. The DC cables are running at +380V and -380V. I was told that this means the phase-to-phase voltage is exceeded if using 600V cable. This generally makes sense, but I think it would be fine using 600V cable. I was also told this violates the "low voltage directive", but I believe that only applies to European countries.

4. On another note, does anyone know of a good training program for solar facility design?

Again, thank you for your time.

You may have an easier time finding answers to these by using the search function. I know I have come across many threads that give opinions about AC + DC together.

IMO the search function on this site is VERY WEAK but if you suffer through it you'll find them.
 
In general AC and DC can be mixed but there may be something in Article 690 that says otherwise. I have not studied that Article.
As far as the voltage, 110.4 would prohibit the use of 600 volt rated conductors on a 760 volt system.
 
Take a look at 300.3(C)(1)
Chris
Buy you also have to look at Article 690 as the rules in there may modify any Chapter 1 though 4 rule. I am not saying there is a rule there, as I have not really looked at the article, but when dealing with installations covered by Chapters 5, 6, and 7 you always have to check there for any modifications.
 
Buy you also have to look at Article 690 as the rules in there may modify any Chapter 1 though 4 rule. I am not saying there is a rule there, as I have not really looked at the article, but when dealing with installations covered by Chapters 5, 6, and 7 you always have to check there for any modifications.

Agreed, I missed the solar part when I first read the original post.

Chris
 