timm333
Senior Member
- Location
- Minneapolis, MN
- Occupation
- Electrical Design Engineer
I have a question for sizing of 125V-DC breaker (as per NEC) which supplies 125V-DC power to the control circuits of ten (10) 4.16kV circuit breakers. The control circuit of each 4.16kV circuit breaker has one trip coil (7.5A DC), one closing coil (2A DC), one spring charging motor (4A DC), and one protective relay (0.2A DC). All 10 breakers are tripped together.
Only protective relays are constant loads, all other loads are momentary loads. For sizing 125V-DC breaker, we will have to take the constant loads and the largest momentary load. Trip coils have the largest momentary loads. We can take 125% load of one (1) trip-coil, and 100% load of the remaining nine (9) trip-coils:
[Constant Loads] + [Largest Momentary Loads] = [10 * 0.2A] + [1 * (125% of 7.5A) + 9 * (100% of 7.5A)] = 2 + 76.88 = 78.88 A.
So 80A 125VDC breaker would be required. Is it correct, what do you guys think about it?
Only protective relays are constant loads, all other loads are momentary loads. For sizing 125V-DC breaker, we will have to take the constant loads and the largest momentary load. Trip coils have the largest momentary loads. We can take 125% load of one (1) trip-coil, and 100% load of the remaining nine (9) trip-coils:
[Constant Loads] + [Largest Momentary Loads] = [10 * 0.2A] + [1 * (125% of 7.5A) + 9 * (100% of 7.5A)] = 2 + 76.88 = 78.88 A.
So 80A 125VDC breaker would be required. Is it correct, what do you guys think about it?