No, the panel source is 480 Vac. I've attached a drawing of how we have designed our drive circuit. The drive is line regenerative. However, after looking at it more, we are trying to apply the following logic, can you tell me if this logic holds:
1) SCCR is by definition a function of symmetrical current.
2) Symmetrical Current is by definition an AC thing.
3) SCCR does not apply to a DC circuit.
No, not exactly.
1) Depends on how you define "a function of ...". The symmetrical current the unit is SUBJECTED to in an AC system is part of the oprocess of determining what SCCR you
need, yes, but is not used in DETERMINING the SCCR. Think of SCCR as the "new and improved" version of what we used to call a "Withstand Rating". WHEN subjected to fault current inside of that unit, will the parts become shrapnel, and will that shrapnel cause collateral damage? That's all it means.
2) True, but irrelevant
3) Not true. SCCR is about SHORT CIRCUIT current, but the although the "symmetrical" does only apply to AC, the term "symmetrical" is not in the definition of SCCR, it's just interested in FAULT CURRENT, be it AC or DC. That's why I asked you if it was fed with AC or DC. If fed with DC, you will need to consider the SCCR of the device with regard to the available DC fault current. But as you are feeding it with AC, then only the AC fault current applies.
So bottom line, in your circuit, the SCCR of that system is the lowest of the fuses, the line reactor, the line contactor and the DC drive rating, unless they were specifically tested and listed in series already. The components on the DC side cannot be subjected to any amount of current in excess of what the rectifier can supply, so even if the components are 5kA, it's irrelevant and more importantly, irrelevant to the rating you must put on the label of the assembly.
It appears you are using an ABB DCS800 DC drive, those are UL listed with an SCCR of 65kA, most contactors are going to have been listed in series with fuses, so unless you picked a reactor that is not listed when protected by fuses, you should be good for 65kA overall.