DC Elevators to AC

Status
Not open for further replies.

bonding jumper

Senior Member
Presently, Con Edison is supplying my clients old building with both ac and dc service, the dc serves the building's 4 elevators. Starting in 2005, Con Ed will no longer be supplying buildings with DC power. What alternitives exist for these elevators? Do they make commercial rectifiers large enough to support elevator motors? What costs could be involved in this? Or do all the motors need to be replaced with ac?
Any imput is greatly appreciated.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: DC Elevators to AC

I've seen elevators that used "motor-generators". An AC motor was used to drive a DC generator that powered the elevator. I've also seen rectifier systems used for elevators.
Don
 

bonding jumper

Senior Member
Re: DC Elevators to AC

Well if anybody is interested I found this article, web page

The power company paid for the conversion? Really :eek: Paid for the rectifiers? or the new ac motors/controls/equipment? Do some power companies have incentives or deals where they would share in the cost of this operation because the want to discontinue dc supply? I'm gonna look into this in other areas as well.

[ August 13, 2003, 04:57 PM: Message edited by: bonding jumper ]
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: DC Elevators to AC

This was about 20 years ago and at the time the POCO was Boston Edison.

As I understood it they paid all costs to provide and install 2 rectifier set ups for elevators in a building I was working in at the time.

It was their choice to discontinue the DC service so why wouldn't they have to cover the costs involved?

I think getting the actual elevator DC motors replaced would be a far greater expense then getting a conveter.

The downtime would be long and you would have to trash the existing DC speed controls and replace them with AC speed controls

Bob
 
Re: DC Elevators to AC

i work on few large industrail areas and they do have both motor-generators and inverters for elevators and large dc motors appacations and it work pretty well in this area. and one of company did have a D.C. power plant inside the bulding for all the large dc motors and elevators and few other stuff tied into

merci marc
 
Status
Not open for further replies.
Top