A DC generator has a no-load output voltage rating of 120v. It's armature ckt. resistance is 0.9 ohms and it's field coils are separately. If load rated @ 2 Kw, @ 115 volts is connected across the output. Neglect all the losses.
What power would be absorbed by the load?
My calculation(s) gives me 1,665 watts.
Solution(s):
Rl = V square / Pr = 6.6125 ohms
Il = E / Ra+Rl = 120 / 0.9+6.6125 = 15.87A
Pl = I square * Rl = 1,665 watts
My question(s) is if I P=IV then;
Pl = 15.87 * 115 = 1,825 watts
1,665 watts is not equal to 1,825 watts; so what happened to the equation? something wrong here? which is the correct answer?
Thank you!!!
Ed...