DC in a fire tower

Status
Not open for further replies.

Rick J

Member
I have been informed that the code (NYC/NEC, Project is in Manhattan) does not allow AC electrical feeders to run through a fire tower, but does this apply to DC feeds as well?

Our client needs to power a remote cabinet located on the 11th floor of a building with the main cabinet on the 32nd floor roof. We will be running a conduit with fiber in the fire tower, then penetrating the wall on the 11th floor and out to the perimeter of the building.

The fiber alone in the conduit appears to be in compliance with the code, but the remote equipment on the 11th floor requires DC power which is typically run with the fiber in the conduit.

Is this allowable by code? What section of the code should I be looking at.

Thanks in advance.

RJ
 
Last edited:

Rick J

Member
More info

More info

Sorry for not being specific. I am referring to the NYC/NEC code. The project is in Manhattan.
 

LawnGuyLandSparky

Senior Member
Rick J said:
I have been informed that the code (NYC/NEC, Project is in Manhattan) does not allow AC electrical feeders to run through a fire tower, but does this apply to DC feeds as well?

Our client needs to power a remote cabinet located on the 11th floor of a building with the main cabinet on the 32nd floor roof. We will be running a conduit with fiber in the fire tower, then penetrating the wall on the 11th floor and out to the perimeter of the building.

The fiber alone in the conduit appears to be in compliance with the code, but the remote equipment on the 11th floor requires DC power which is typically run with the fiber in the conduit.

Is this allowable by code? What section of the code should I be looking at.

Thanks in advance.

RJ

For what purpose do you think running feeders through fire towers is prohibited?
 

Rick J

Member
The NYC building code states that no piping can be run through an egress stair. And most fire towers are part of an egress stair.

I have attached a portion of the code.

It may be dependent on definition of the term "piping".
 
I would be very surprised if the BEC would permit the installation you are trying to install. They are very serious when it comes to the raceways in the stairwells.
I was brought into a job in NYC that had a 4 inch raceway installed in the stairwell up 17 stories. The entire installation was removed.
 