DC Siren Motor blows fuse about once per year. Usually we replace the fuse and leave. Today I had my help amp clamp the DC side when it cycled for the 'noon whistle'. No more than 5 seconds run. Meter was set on 'Inrush'. Flukes terminology for the setting used. Capture was 468 amps DC. Rectifier output, two diodes, was the 48VDC listed output. He did not have time to switch meter to collect run amperage. Nominal operating current is 100 amps, via specs.
Does a DC motor have an inrush? I thought not, but have never looked for it before. Across the line start on load side of power supply.
468 amps would explain the occasional fuse blowing as the time current curve for the fuse used shows 10 seconds for 500 amps.
This is the only siren of its type that we have this problem with.
Does a DC motor have an inrush? I thought not, but have never looked for it before. Across the line start on load side of power supply.
468 amps would explain the occasional fuse blowing as the time current curve for the fuse used shows 10 seconds for 500 amps.
This is the only siren of its type that we have this problem with.