Re: DC Power Grounding
John, I think I can help since I design DC power plants and protective grounding. First thing we need to make clear is that AC equipment ground and DC equipment grounds are two separate systems with a common bond.
Question: Is the DC "logic ground" required to be "bonded" to the frame ground?
Answer: Yes, but probable not in the way you are thinking. A DC plant usually has a Master Ground Bus (MGB) associated with it, and serves as the Isolated Ground Plane (IGP) Single Point Ground (SPG). The source ground for the MGB comes from the Office Principle Ground Point Bus (OPGPB). This "source ground" is the same as a GEC in an AC system, and is typically a 750 KCM.
The MGB has a Main Bonding Jumper (MBJ) connected to the return bus of the DC power plant sized to a formula based on the number of rectifiers and batteries (typically 750 KCM). The MBJ serves the same purpose as the MBJ in an AC system connecting the grounded conductor to the Ground Electrode System (GES), in order to allow OCPD?s to operate.
As I said before the MGB serves as the SPG for the DC system. The Logic Ground Bus (LGB) originates from the MGB but is isolated from the Frame Ground Bus (FGB). The LGB purpose is to serve as a current free signal reference for data bit detectors.
The FGB originates from the MGB. The FGB purpose is the same as an AC EGC circuit. It is a current free fault-clearing path for the OCPD?s.
There are no ground loops if designed and installed correctly. That is why it is called an ?Isolated Ground Plane?.
A 24-volt system is not required to be referenced to earth, but there is still the requirement to provide over current protection for the system. If you did not reference one of the battery polarities to something (say a piece of metal magically floating in air) or earth, you would have to provide a Ground Fault Detection (GFD) system, and OCPD on both battery polarities in the primary and secondary protection systems. It is much less expensive and complicated to reference to earth, provide a common fault-clearing path, and only provide OCPD?s in the ungrounded conductor.
Question: Also, any good reference books or references for topics such as this? DC power seems to be pretty well neglected when you get into low-voltage high current areas.
Answer: Yes for a price. It is proprietary information. Some sources are Tellcordia, BICSI, ANSI/IEEE, and telephone operating companies. The best is from Tellcordia (TR-NWT-000295 Titled ISOLATED GROUND PLANES) in which all others are based upon. I also have written a engineering/installation practice for an operating company.