gonzoleroy
- United States
I maintain a lab that utilizes a -48 VDC system for telecom equipment. The system was installed ~12 years ago. Nearly all of my experience is with AC power, so I am fairly unfamiliar with DC requirements as governed by the Code.
While addressing a request to add additional drops to the lab it was brought to my attention that all of the 100 or so DC circuits in this lab are supplied with standard #6 Cu, THHN via VertiRack--and protected by 100-amp circuit breakers. As a raceway type of guy, this level of current on #6 immediately bothered me, so I dove into the NEC to gain understanding.
It seems that whomever designed this lab referred to Table 310.17 for allowable ampacity--which specifies "Conductors...In Free Air". Have a look at distribution in these Vertiracks:
There is clearly no spacing maintained, the conductors are simply bundled onto the Vertirack. How can Table 310.17 be used in this instance?
Article 392.11(B) mentions ampacity for sizes 1/0 and above, and also describes the required spacing. Am I missing some provision for wire sizes smaller than 1/0 AWG?
Any help you guys can provide is appreciated.