Sluker, here is my reply to your e-mail.
I design DC plants for telephone offices at 48 VDC @ 10,000 amps. We determine the cable size by voltage drop at DC and not current. In your case 6 volts is extremely low so voltage drop will be critical with the high current. The formula is:
CM = (22.2 x I x L)/VD
Where
CM = Circular Mills of Cable
I = Load current in Amps
L = Length one-way distance in feet
VD = Voltage Drop
After you perform the calculation you will need to compare it to the appropriate table in 310 to make sure you do not exceed the requirements. This is not normally a problem unless the length is very short; say less than 10 to 20 feet.
By looking at Table 310.17 (free-air) the minimum size using four cables is 700 MCM. My guess for voltage drop would be 1/8 volt or less.
So lets run a sample.
I = 3000
VD = 1/8 = .125
Length one way = 10 feet
CM = (22.2 x 3000 x 10)/.125 = 5328 KCM
Take 5328 KCM divide by 4 = 1332 KCM. Closest match is 4-1250 KCM cables. This exceeds the minimum requirement of even Table 310.16 @ 75 degree table.