I was wondering about bringing DC back to the house vs locating the inverters by the arrays.
If the wire is rated at [say] 300V AC,
what's the Code say about DC, given the AC is in RMS?
………..
Equivalent.
…………
Ok so thats around 300 amps 240 AC. Two sets of 500 AL may do it (depending on what you want for voltage "rise"). I just ordered some triplexed 500-500-/1/0 and it was$3.60 a foot. Fronius inverters do 1kv strings so you could try the math on that. Remember PV wire is available in AL too. I recently did two systems that were long runs but not as big (600 feet 20kw, 800 feet 10 kw) and
did not find it worthwhile to run the DC back, even with 1kv strings.
……………
.
You/he will have to price out the
cost of running multiple #10 or #8 strings back to the house versus running some massive sets of aluminum. Pulling the string wiring will likely be easier than 500 kcmil aluminum.
…
...
It may be difficult to utilize the existing #2 for DC given typical residential inverter equipment nowadays. That decision will likely be determined by what you can find to work with it rather than what is theoretically most efficient.
……….
In other words, you might be kind of forced to use it for AC and put inverters at the building with the arrays.
………..
My response to above comments:
Most comments are not accurate.
There is a definite difference between current capacity of a given size of conductor when passing energy on DC versus AC.
DC doesn’t suffer from reactance which ultimately cause reduced current flow—that is passing through a conductor. This is mostly affected by SKIN EFFECT and to a lesser extent . . . PROXIMITY EFFECT. The latter is induced by induction caused by AC current.
Both of these phenomena don’t happen in DC circuit.
The formula for impedance provides another way to show these relationships:
i
mpedance= square root of resistance in ohms squared + (inductive reactance in ohms minus capacitive reactance in ohms squared)
Other factors that are present in AC circuits--that are not present in DC circuits also include
frequency and inductance.
The higher the frequency, the more pronounced effect the above equation has on the overall current capacity of a conductor.
Check these links for starter:
https://waveguide.blog/impedance-skin-effect-implications-high-frequency-circuits/
ht
tps://electricalbaba.comh/cause-of-skin-effect-in-ac-conductors/
https://electricalbaba.com/comparison-of-ac-and-dc-transmission/
Yes, as alluded to by another poster-- multiple runs of smaller conductors could mitigate the adverse anomaly that SKIN EFFECT or PROXIMITY EFFECT has on current flow. But could be cost- prohibitive. This approach is often called the Litz Effect but is more effective on electronics, inductors and switching transformer circuits.
There is a lot to say about
skin effect but that would be better covered from a different platform.
In summary:
Running DC from the array to the house has benefit than running AC--after the inverter that is located in the vicinity of the DC source.