wirenut1980
Senior Member
- Location
- Plainfield, IN
Good morning! I have a customer with a technician who claims to have measured 7-8 V DC on an AC utility supply. They measured line to line on a single phase 120/240 V service with a Fluke handheld meter (the model # escapes me). A week earlier, this customer had a large UPS fail several batteries. The UPS technician is the one who originally measured the DC voltage. He is claiming that the DC voltage failed the batteries.
A few days later, I was called out to investigate. The technician and I were unable to measure the DC voltage at this time.
Some additional background information: this is a communications tower with a few companies that have equipment attached. AT&T is one company and they have some DC equipment.
Also, a couple weeks ago, there was some sort of surge event that took out some surge protectors. I don't know if it was lightning or not. I think it is more likely this surge is what is responsible for failing the batteries rather than 7 V DC.
My first question is it possible to measure DC voltage on an AC supply using something like a Fluke 87? Next, any thoughts on where the DC might have come from if it was really there? One theory is a rectifier on AT&T equipment went bad and was dumping DC voltage back on the supply. AT&T comes out and replaces their equipment without telling anyone and the voltage is gone when I get there later.
I do have a PQ monitor that can measure 0-600 V DC and record over time. I think I am going to hook it up to the incoming 240 V AC and see if it measures anything.
Any thoughts are appreciated.
A few days later, I was called out to investigate. The technician and I were unable to measure the DC voltage at this time.
Some additional background information: this is a communications tower with a few companies that have equipment attached. AT&T is one company and they have some DC equipment.
Also, a couple weeks ago, there was some sort of surge event that took out some surge protectors. I don't know if it was lightning or not. I think it is more likely this surge is what is responsible for failing the batteries rather than 7 V DC.
My first question is it possible to measure DC voltage on an AC supply using something like a Fluke 87? Next, any thoughts on where the DC might have come from if it was really there? One theory is a rectifier on AT&T equipment went bad and was dumping DC voltage back on the supply. AT&T comes out and replaces their equipment without telling anyone and the voltage is gone when I get there later.
I do have a PQ monitor that can measure 0-600 V DC and record over time. I think I am going to hook it up to the incoming 240 V AC and see if it measures anything.
Any thoughts are appreciated.