De-Rate: Greater than three conductors or phases

Status
Not open for further replies.
Suppose Panel A feeds Panel B, and the voltage is 208/120/3 Phase, Y-Connected. Now, if you send the three phases plus neutral to feed Panel B, and Panel B is mostly made up of 120 non-linear circuits, does the neutral count as a conductor? Must the wire in the conduit feeding Panel B de-rated? Or, does the de-rate only happen when you have more than three "going in the same direction"? Meaning, the neutral current is traveling in opposite direction of the phase conductors.
 
Is there any kind of ratio that you can apply to a panel and deem the neutral a current carrying conductor? In the example I used, something like if the ratio of (120V circuits)/(1phase and 3phase) > some number, than consider the neutral a conductor?
 
ctrane said:
Is there any kind of ratio that you can apply to a panel and deem the neutral a current carrying conductor? In the example I used, something like if the ratio of (120V circuits)/(1phase and 3phase) > some number, than consider the neutral a conductor?


The NEC uses the words "major portion" of the load being non-linear to describe when the neutral counts as a CCC in a 208Y/120 volt system. If the non-linear loads were greater than 50% of the total load than the neutral would count as a CCC. 50% or less, it does not count.


310.15(B)(4)(c) On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral shall therefore be considered a current-carrying conductor.
 
Well, it sounds as though 310.15(B)(4)(b)&(c) describe your situation to a tee. So, you will be well advised (if not obliged) to consider the neutral a CCC.

Lowering the estimated load on that neutral will not achieve any breaks in terms of derating; your ungrounded conductors will need to be upsized right along with the neutral.

It sounds as though you're willing to kick the ungrounded conductors up a notch, but want to keep the neutral small. Why?

Edit to correct reference
 
Status
Not open for further replies.
Top