Here is the question... I have an existing 1-1/2 (over 24") conduit with with 35 #10 THHN, all CCC's supplying 20amp loads, will this pass inspection?
#10 THHN good for 40amps
31-40 adjusted to 40% = 16amps
next breaker size 20 amps
I have seen this pass in the past and but I'm getting different answers when asking around. Would greatly appreciate you're feed back.
#10 THHN good for 40amps
31-40 adjusted to 40% = 16amps
next breaker size 20 amps
I have seen this pass in the past and but I'm getting different answers when asking around. Would greatly appreciate you're feed back.