I'm looking for an exception in the NEC to de-rate a Class 1, Div II area. I've understood that all equipment/instrumentation can be de-rated to "non-hazardous" within a 25' sphere of an open flame (i.e. = natural gas pilot in operation).
Where is this exception explained within the NEC - Article 500?
Also, is this exception acceptable under IEC - ATEX standards?
Industrial Example: Subistute a NEMA 4 enclosure in place of NEMA 7 within this 25' sphere.