This latest machine has 24 VFD's driving various size motors for different operations. The material is fed trhough the machine at a constant rate, though the operations along the way are sometimes "Stop n Go" operations. Material flow is constant.
Using my mormal method of adding up the current requirements Per the VFD manufacturers spec manuals, and considering the control voltage etc. and arriving at a full load rating of 379 amps. I have a 400 amp fused disconnect installed.
Now my boss (Company Owner) Has basically ordered me to derate this FLA to 250 Amps.
His reasoning is these motors will never run all at the same time and not at full load. "So we have to come up with a spreadsheet to show percentages of duty, and derate the machine accordingly"
Will it run on 250 Amps ? Probably ! But that doesn't give me any legal right to just "Make up" a number. with no data to support the Derate.
Is this done normally in determining FLA's ? Or is he going to get us all in a mess ?
Using my mormal method of adding up the current requirements Per the VFD manufacturers spec manuals, and considering the control voltage etc. and arriving at a full load rating of 379 amps. I have a 400 amp fused disconnect installed.
Now my boss (Company Owner) Has basically ordered me to derate this FLA to 250 Amps.
His reasoning is these motors will never run all at the same time and not at full load. "So we have to come up with a spreadsheet to show percentages of duty, and derate the machine accordingly"
Will it run on 250 Amps ? Probably ! But that doesn't give me any legal right to just "Make up" a number. with no data to support the Derate.
Is this done normally in determining FLA's ? Or is he going to get us all in a mess ?