De-rating of conductors

Status
Not open for further replies.

tonype

Senior Member
Location
New Jersey
Does 310-15 apply to a bundle of cables tied together, tightly, with zip ties that are not in a conduit, cable tray or running through floor joists? My interpretation is yes. I saw an installation where up to 19 Type-NM's (minimum 12) were bundled together and routed above a garage door and along side the entire main beam in to the home. Total length was about 40 feet.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
THey added a bit of wording in '08 {310.15(B)(2)} to help clarify that:

(a) More Than Three Current-Carrying Conductors in a Raceway or Cable. Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 600 mm (24 in.) and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)(2)(a). Each current-carrying conductor of a paralleled set of conductors shall be counted as a current-carrying conductor.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Does 310-15 apply to a bundle of cables tied together, tightly, with zip ties that are not in a conduit, cable tray or running through floor joists? My interpretation is yes. I saw an installation where up to 19 Type-NM's (minimum 12) were bundled together and routed above a garage door and along side the entire main beam in to the home. Total length was about 40 feet.

Sounds like bundling to me; therefore derating would need to be applied or the cables would need to be reinstalled with spacing between them.
 