If I have outlets for in sink disposals, microwaves, refridgerators ect, I am not allowed to take 50% of the load above 10,000 and I have to count each receptacle at the VA of the equipment.
Is there any de-rating factor I can use when figuring the load on the transformer? We did a project where we calculated the above loads as 100% and then did the derating on the general convenience receptacles.
We had a data logger watching the load on the transformer for a week(EE type transformer) We are peaking at about 40% of the calculated load.
The peak came at noon when everyone was using the microwaves. EE transformers are designed for 35% load on a 24 hour average, and the night time load was only around 4-6% depending on the day. Most of the day the load was running about 20% to maybe 26%.
That makes me think that either everybody ends up with oversized transformers, or there is a derating factor I am missing.
Is there any de-rating factor I can use when figuring the load on the transformer? We did a project where we calculated the above loads as 100% and then did the derating on the general convenience receptacles.
We had a data logger watching the load on the transformer for a week(EE type transformer) We are peaking at about 40% of the calculated load.
The peak came at noon when everyone was using the microwaves. EE transformers are designed for 35% load on a 24 hour average, and the night time load was only around 4-6% depending on the day. Most of the day the load was running about 20% to maybe 26%.
That makes me think that either everybody ends up with oversized transformers, or there is a derating factor I am missing.