Art. 338.10(B)(4) states 60C when used as a feeder.
Southwire makes a 90?c SER, so the 2011 NEC 338.10(B)(4) now limits SE ampacity in accordance with 60?c ratings, when in contact with thermal (building) insulation, in addition to cable bundling, 334 section II.
..T.310.15(B)(6) makes no mention of temp and specifically allows se cable. If you look at the table all those conductors and wire types are 75?c or better but again the Table makes no mention of temp. We might infer that but IMO it is not written and there is no reason 338.10 should override this table.
I agree with Augie that many contractors & AHJ's relying on NFPA tables may have overheated cable, devices, enclosures, PVC & liquidtight raceway for years this way.
Augie47 said:
The entire situation is ridiculous and there are so many opinions since many read the Code differently.
338.10(B)(4)(Note 1) refers to other codes for wire-insulation temperature, engineered or table-derating methods, and 110.14(C). The NFPA handbook's commentary on 110.14(C), describes how this issue results in overheated equipment.
NFPA70 handbook Tenth Edition p.68 said:
When equipment of 600 volts or less is evaluated relative to the appropriate temperature characteristics of the terminations, conductors sized according to Table 310.16 are required to be used. The UL General Information Directory (White Book, page 3) clearly indicates that the 60?C and 75?C provisions for equipment have been determined using conductors from Table 310.16. However, installers or designers unaware of the UL guide card information might attempt to select conductors based on a table other than Table 310.16, ...That use can result in overheated terminations at the equipment. Clearly, the ampacities shown in other tables, such as 310.17 could be used for various conditions to which the wiring method is subject (ambient, ampacity correction, etc.), but the conductor size at the termination must be based on ampacities from Table 310.16. This change does not introduce any new impact on the equipment or the wiring methods; it simply adds a rule from the listing information into the Code because it is an installation and equipment selection issue.
If UL tells us, "no other table overrides 310.16 where conductor-termination temp. is concerned," then equipment must be listed for 310.16-adjusted temperatures, regardless of other tables. Designers, installers, & inspectors that miss this rule are most likely to overheat equipment.
Failures and liabilities from new electrical installations remain prolific enough to sustain cottage industries for thermal-camera imaging, expert-fire investigators, and litigators for bad-faith insurers denying claims.
The industry practice of avoiding engineering supervision, internationally-recognized formulas (IEEE), and standards (ICC), has relied instead on NFPA ? ampacity tables, factoring multiple adjustments, without temperature hierarchy, and derating schemes that treat inductive & resistive loads equally.
When equipment is overheated this way, NFPA ? ampacity tables for idiots makes everyone equal, since its difficult to distinguish licensed operator from their unskilled employee, or exploited laborer from unlicensed handyperson, side worker, or trunk slammer. Inspectors should approach everyone indoctrinated by the NEC with equal caution & skepticism.