kgk1961
Member
- Location
- Georgia, USA
We are currently installing a project working at the direction of a plant engineer. The equipment that we are installing only has four (4) connection points; three ungrounded conductors and a grounding conductor (480V, 3-phase). This accounts for 95% of the project. The other 5% consists of mostly 277V lighting, which is fed from a separate panelboard dedicated for lighting. (It is an existing facility and 120V is already in place from another source.) Therefore, majority of the panelboards are dedicated solely to providing power to the equipment that is being installed, all of which is 480V 3-phase (with NO neutral connection point).
The engineer has come to us and requested that we add a neutral conductor from the main switchboard to each of the panelboards "just in case" something comes up in the future and they need 277V for controls. He has gone on to direct us to "de-rate" the neutral conductor to 60% of the ampacity of the ungrounded conductors.
:jawdrop:
Is this premissible per the NEC?
How did he come up with 60%?
The engineer has come to us and requested that we add a neutral conductor from the main switchboard to each of the panelboards "just in case" something comes up in the future and they need 277V for controls. He has gone on to direct us to "de-rate" the neutral conductor to 60% of the ampacity of the ungrounded conductors.
:jawdrop:
Is this premissible per the NEC?
How did he come up with 60%?