When de-rating UF (and other insulation types) do you still use the 90*C column or the 60*C column?
340.80 Ampacity. The ampacity of Type UF cable shall be
that of 60°C (140°F) conductors in accordance with 310.15.
340.112 Insulation. The conductors of Type UF shall be
one of the moisture-resistant types listed in Table
310.104(A) that is suitable for branch-circuit wiring or one
that is identified for such use. Where installed as a substitute
wiring method for NM cable, the conductor insulation
shall be rated 90°C (194°F).
334.80 Ampacity. The ampacity of Types NM, NMC, and
NMS cable shall be determined in accordance with 310.15.
The allowable ampacity shall not exceed that of a 60°C
(140°F) rated conductor. The 90°C (194°F) rating shall be
permitted to be used for ampacity adjustment and correction
calculations, provided the final derated ampacity does not exceed
that of a 60°C (140°F) rated conductor. The ampacity of
Types NM, NMC, and NMS cable installed in cable tray shall
be determined in accordance with 392.80(A).
Using the 340.10 reference that Bryan cited, yes. Inside could be 90C.
Outside is definitely 60C.
Odd way to do it imo.
Just to confirm, using table 310.15(B)(2)(a), if I had #6 UF, Id pick 55amps from table 310.15, and with an ambient between 31-35*C I multiply 55 by 0.91= 50amps, so my load is restricted to 50amps.