NEC Table 316(B)(2)(a) requires de-rating the ampacity of the conductors when more than three current-carrying conductors are in a raceway. I had a specific situation that sparked a discussion. I had #12 THHN in 1" conduit with a 20 amp. breaker. 40% fill says you could have 26 wires but the above table seems to limit you to 9 current carrying conductors, meaning four single-phase branch circuits.
Everyone seems in agreement on the 40% fill, but I've had some pushback on the conduit size not enetring into the equation.
I could find no place in the NEC that modifies this de-rating in any way due to the size of the conduit.
In other words, I'd be limited to 4 single-phase circuits regardless of whether I put them in 3/4" or 4" conduit. Is that correct??