Dead mans leg

Maustin15

Member
Location
Oklahoma
Occupation
Electrician
Ok so I came across a dead man’s leg system at a golf course. Anyone want to shed some light on this topic


Sent from my iPhone using Tapatalk
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
A corner grounded system is actually not much different than grounding the center of a winding. You are establishing the first fault in an electrical source so the next fault will force the OCPD to trip.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Zero is correct on 1 leg if metering to grounded conductor of the corner grounded Delta. All phase to phase should be reading full voltages, 480V.

 
Top