Dead Tank Circuit Breakers

Status
Not open for further replies.

zog

Senior Member
Location
Charlotte, NC
Dear Forum Members,
What are the test to be done for dead tank circuit breaker which is 30 Years old
Your quick response is highly appreciated
Alex @ Arjun

Gas analysis, time travel, DLRO across contacts and bolted connections, Hipot. Those are the basics, check your local standards because I assume they are different than North American test standards.
 

Ingenieur

Senior Member
Location
Earth
a dead tank = the tank around the contacts is grounded
a live tank means the tank is at line potential

OP, I would contact a testing agency or contractor, they can give you a checklist
 