peter d
- New England
The same church from my baptismal pool thread also has a small 600 volt system to feed several air conditioning units from the early 1970's.
The service is 120/208 with 2 small transformers to obtain 600 volts. From a visual inspection, I can see many problems:
The units (ancient Carrier unitary water cooled types) are in horrible shape with covers missing, live parts exposed, no ground wires run, etc.
The conduit feeding the units has separated in several places, and of course the conduit has no ground wire.
One transformer has no GEC.
The other transformer is hard piped, they used EMT for the ground wire, and the pipe enters the transformer through reducing bushings.
I told the pastor that the entire system needs to be ripped out and thrown away, but they still use the AC units and they are badly needed in the summer. It will be a while before they get enough money to replace them, so they will have to stay for now.
Any suggestions on how to make this safe? Money is tight of course, and fortunately the units don't get used much.
[ September 26, 2005, 04:15 PM: Message edited by: peter d ]