Senior Member
WAs having a conversation with some over articles NEC 210.21 (2), 210.23. I always believe that 210.21(2) "Total Cordand plug connected load" was dealing with all the loads from all of the receptacles that could not be over 80% . For example, you have a microwave plugged into one 20 amp receptacle and down the line you have a toaster plugged into another receptacle located somewhere else and their COMBINED loads go over 16amps on that branch circuit, creating a code violation.
But after reading that section again, I dont think it says that because of '.... a receptacle shall not supply a total cord and plug connected load in excess of maximum specified in table 2110.21(B)(2).
It says receptacle and NOT branch circuits. It just seems redundant of what 210.23 (A) (1) says. what do you think?? why do they need both sections??