Deck box distance from pool? AND

Status
Not open for further replies.

ritelec

Senior Member
Location
Jersey
Reading in 680.
Deck box with or without 120v transformer has a minimum horizontal spacing of 4 ft.

Correct ?

Pool guy says it has to be 10 feet. And the reason it can be closer is if it where " under "
The diving board.

Please confirm. Thank you

Also. Rather than another post and I'm sure it's probably even talked about before.
But perimeter bond. Below subgrade ? What if final grade was going to be a cinder block or pavers ?

Reason I ask is I believe the grade on this install is dirt and grass.
What's the subgrade depth for perimeter bonding ?

Thanks again.
 
Luminaire over 15 volts
horizontal spacing: 4 ft from inside wall of pool unless separated by solid fence, wall or permanent barrier.
 
Status
Not open for further replies.
Top