Would the MOP spec of 25A on each of the 3 phases be the OCPD breaker trip to use???
I am not sure I fully understand where the linearity/pf is specified.
The full spec is at the link but to make it easy I have abstracted below the electrical power specs of interest and put in my questions in underscored italics.......
Rated Cooling Capacity (Btu/hr): 110,000 Rated Heating Capacity (Btu/hr): 126,000
Nom Cooling Capacity (Btu/hr): 120,000 Nom Heating Capacity (Btu/hr): 135,000
Cooling Input Power (kW): 8.21 Heating Input Power (kW): 12.40
OUTDOOR UNIT DETAILS
Power Supply (V/Hz/Ph): 460 / 60 / 3 Compressor Type Inverter.....so it is nominal 480v 3 phase 60Hz???
Power Supply Connections: L1, L2, L3 Ground
Capacity Control Range (%): 10 - 100......... what does this mean???
Min. Circuit Amps MCA (A): 21.10......... what does this really mean???
Max Overcurrent Protection (MOP) (A): 25.00 ......... does this mean use 25A breaker for OCPD on each phase???
Rated Load Amps RLA(A): 6.8+6.8 .........This is cryptic..does this mean that under normal operation it uses 2x6.8A = 13.6A???
Full spec sheet is here:
http://www.daikinac.com/content/assets/DOC/SubmittalDataSheets/VRV/REYQ/460v/SDS-REYQ120TYDN.pdf
I am not sure I fully understand where the linearity/pf is specified.
The full spec is at the link but to make it easy I have abstracted below the electrical power specs of interest and put in my questions in underscored italics.......
Rated Cooling Capacity (Btu/hr): 110,000 Rated Heating Capacity (Btu/hr): 126,000
Nom Cooling Capacity (Btu/hr): 120,000 Nom Heating Capacity (Btu/hr): 135,000
Cooling Input Power (kW): 8.21 Heating Input Power (kW): 12.40
OUTDOOR UNIT DETAILS
Power Supply (V/Hz/Ph): 460 / 60 / 3 Compressor Type Inverter.....so it is nominal 480v 3 phase 60Hz???
Power Supply Connections: L1, L2, L3 Ground
Capacity Control Range (%): 10 - 100......... what does this mean???
Min. Circuit Amps MCA (A): 21.10......... what does this really mean???
Max Overcurrent Protection (MOP) (A): 25.00 ......... does this mean use 25A breaker for OCPD on each phase???
Rated Load Amps RLA(A): 6.8+6.8 .........This is cryptic..does this mean that under normal operation it uses 2x6.8A = 13.6A???
Full spec sheet is here:
http://www.daikinac.com/content/assets/DOC/SubmittalDataSheets/VRV/REYQ/460v/SDS-REYQ120TYDN.pdf