hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have decorative fountain back of two story building. The panel board P1 is inside the building that has feeder breaker which feeds to outside Panelboard P2 mounted outside the building on pressure treated board 2” x 8” supported by posts 4”x4”. MLO Panelboard P2 has branch circuits which feed fountain lights low voltage 12VAC xfmr in between, Filter pump, Feature Pumps total of 5.
The decorative fountain will not be used for swimming, wading, immersion or therapeutic purposes. So basically it is not pool per definition of pool. It is isolated does not have water common to pool.
Questions:
1. See attached which still show fountain reinforcing steel bonded with steel wire which is bonded to all metal pipes, metal gutter by #8 AWG which then goes to recirculation equipment next to the panel board P2. I am not sure why this would be provided. This is not a pool it is decorative fountain no swim, wading, immersion, therapeutic purpose. Is it because of NEC 2014 section 680.54? If not then is this required by code and what section?
2. If it is not required by code would it hurt to have attached sketch?
3. Panel board P2 should have main breaker?
4. Panel board P2 should it have grounding electrode system per NEC 2014 section 250.32? No main bonding jumper?
The decorative fountain will not be used for swimming, wading, immersion or therapeutic purposes. So basically it is not pool per definition of pool. It is isolated does not have water common to pool.
Questions:
1. See attached which still show fountain reinforcing steel bonded with steel wire which is bonded to all metal pipes, metal gutter by #8 AWG which then goes to recirculation equipment next to the panel board P2. I am not sure why this would be provided. This is not a pool it is decorative fountain no swim, wading, immersion, therapeutic purpose. Is it because of NEC 2014 section 680.54? If not then is this required by code and what section?
2. If it is not required by code would it hurt to have attached sketch?
3. Panel board P2 should have main breaker?
4. Panel board P2 should it have grounding electrode system per NEC 2014 section 250.32? No main bonding jumper?