Ok, heres the deal: New School, owner wants emerg lights / exits, coolers, freezers, fire alarm, security system, UPS, and fire pump, on generator.
It is pretty clear that 700.6(d) requires the fire pump and emerg lights / exits on a separate transfer switch from the coolers, and freezers. I am not questioning if you have to do it but why.
If the generator is sized to run all the loads simultaneously, what does the second transfer switch get you? Is it that it insures separation of loads?? Same Generator to fail or run out of gas, or have a dead battery. Whats most likely to fail the generator or the transfer switch? Separate ATS are not redundant so no benefit there. I suppose a short in the feed to a non-emergency load could open the upstream breaker for the emergency loads if the breakers are not well coordinated.
There is a lots of extra expense for two generator backed distribution systems throughout a large facility. It seems that the code is really pushing design toward battery packs (ATS for fire pump is normally integral to controller and thus separate). Leaving the generator suppling only optional loads.
The owner's maintenance staff ends up with a school full of integral batteries or wall warts that have to be maintained. Nice.
It is pretty clear that 700.6(d) requires the fire pump and emerg lights / exits on a separate transfer switch from the coolers, and freezers. I am not questioning if you have to do it but why.
If the generator is sized to run all the loads simultaneously, what does the second transfer switch get you? Is it that it insures separation of loads?? Same Generator to fail or run out of gas, or have a dead battery. Whats most likely to fail the generator or the transfer switch? Separate ATS are not redundant so no benefit there. I suppose a short in the feed to a non-emergency load could open the upstream breaker for the emergency loads if the breakers are not well coordinated.
There is a lots of extra expense for two generator backed distribution systems throughout a large facility. It seems that the code is really pushing design toward battery packs (ATS for fire pump is normally integral to controller and thus separate). Leaving the generator suppling only optional loads.
The owner's maintenance staff ends up with a school full of integral batteries or wall warts that have to be maintained. Nice.