Dedicated Electrical "Building" Fire Rating

Status
Not open for further replies.

scrub12

Member
Location
Cleveland, OH
Occupation
Electrical Engineer
Do the NFPA standards or building code separate the fire rating and sprinkler requirements for a standalone electrical building separate from any other building? I am installing a pre-fabricated electrical building that only includes two Motor Control Centers and a 1200A switchboard. The room is not going to have sprinkler protection. The question is, does the building need a 2-hour fire rating?
 
Electrical equipment doesn't affect the fire rating until you get a big transformer (150 kVA) in the space. The architect should be able to tell if it can be unrated construction.
 