Dedicated Electrical Space above equipment

Status
Not open for further replies.

Grouch

Senior Member
Location
New York, NY
Happy Friday all!

I have a question on dedicated electrical space, based on 2008 NEC, section 110.26.F.1.a. I know there's other threads on this, but couldn't find my particular questions.

1) The space equal to 6 feet above electrical equipment, where there can't be any foreign equipment in this space... does this apply to panels in apartments / dwelling units? I assume it does. There is central AC, so ductwork is present in some areas, and we're looking at placing the panels on the wall with ductwork penetrating the wall above... I have room to move the panels left or right to avoid the ductwork, but just wanted to check if this section applies here.

2) As an extension of the question above, if we recess the panels into the wall, with ductwork above, are we still in violation of 110.26.F.1.a? Not sure if recessing panels gets you around the problem.

Thanks!
 
I only have my 2011 handy. It say no ducts shall be in the zone above the panel. It also says the zone is equal to the width and depth of the panel so a recessed panel with a duct in front of it (but not over it) sounds OK.
 
Recessing the panels does not get around the situation if the ducts or pipes are in the vertical wall space above it.
If they just run next to the wall it would be a potential working space violation instead.

Sent from my XT1585 using Tapatalk
 
Happy Friday all!

I have a question on dedicated electrical space, based on 2008 NEC, section 110.26.F.1.a. I know there's other threads on this, but couldn't find my particular questions.

1) The space equal to 6 feet above electrical equipment, where there can't be any foreign equipment in this space... does this apply to panels in apartments / dwelling units? I assume it does. There is central AC, so ductwork is present in some areas, and we're looking at placing the panels on the wall with ductwork penetrating the wall above... I have room to move the panels left or right to avoid the ductwork, but just wanted to check if this section applies here.

2) As an extension of the question above, if we recess the panels into the wall, with ductwork above, are we still in violation of 110.26.F.1.a? Not sure if recessing panels gets you around the problem.

Thanks!
Did not look to verify, but seems it mentions the six feet but also only applies up to the "structural ceiling". If duct were in the structural ceiling but less then 6 feet above, it would still be permitted to be there, could require leak protection if it were something that may leak though.
 
Recessing the panels does not get around the situation if the ducts or pipes are in the vertical wall space above it.
If they just run next to the wall it would be a potential working space violation instead.

Sent from my XT1585 using Tapatalk

I was afraid that was the answer... recessing the panels doesn't get around the violation.
 
I only have my 2011 handy. It say no ducts shall be in the zone above the panel. It also says the zone is equal to the width and depth of the panel so a recessed panel with a duct in front of it (but not over it) sounds OK.

yeah, I figured the section would apply to apartments as well. thanks.
 
Did not look to verify, but seems it mentions the six feet but also only applies up to the "structural ceiling". If duct were in the structural ceiling but less then 6 feet above, it would still be permitted to be there, could require leak protection if it were something that may leak though.

ductwork is below the structural ceiling unfortunately.
 
Did not look to verify, but seems it mentions the six feet but also only applies up to the "structural ceiling". If duct were in the structural ceiling but less then 6 feet above, it would still be permitted to be there, could require leak protection if it were something that may leak though.
The way you worded this has me confused over what you intended to say. So let me say it this way:

  • If the structural ceiling is less than 6 feet above the top of the panel, then no ducts or pipes can be above the panel.
  • If the structural ceiling is more than 6 feet above the top of the panel, then a duct or pipe can be run over the panel, so long as it is more than 6 feet above the top of the panel, and so long as you install a drip shield.

Is that what you were trying to say?

 
The way you worded this has me confused over what you intended to say. So let me say it this way:
  • If the structural ceiling is less than 6 feet above the top of the panel, then no ducts or pipes can be above the panel.
  • If the structural ceiling is more than 6 feet above the top of the panel, then a duct or pipe can be run over the panel, so long as it is more than 6 feet above the top of the panel, and so long as you install a drip shield.

Is that what you were trying to say?

I don't see it that way.

2014 - 110.26(E)(1)(a):

Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone

Structural ceiling is the bottom of joists or trusses above you on the level of the building you are on. A foreign system can run in the space above the structural ceiling even if the equipment requiring dedicated space is right up to the structural ceiling. Might not be a good idea design wise but is NEC compliant.

If that foreign system is subject to leaks, condensing, etc. you would still need to provide protection from such things, but such protection can not be within the dedicated space - so the protection would also need to be within the structural ceiling on many low ceiling applications.

Exception that follows allows suspended ceilings with removable panels in said zone but they are not part of the structural ceiling, so the dedicated space extends past a suspended ceiling.

ADD:

A panel in a basement of a house could have foreign system less then six feet above it if that foreign system is "within the floor joists", as those floor joists is the structural ceiling.
 
Last edited:
OK, kwired. I see how we are appearing to disagree with each other. But we are not. This is one of those famous arguments that goes like this:
Person 1 says, "The grass is green."
Person 2 says, "No, you are wrong. The sky is blue."

So let me revise my earlier post to clarify (revised wording is in bold, red text):

  • If the structural ceiling is less than 6 feet above the top of the panel, then no ducts or pipes can be between the top of the panel and the bottom of the structural ceiling.
  • If the structural ceiling is more than 6 feet above the top of the panel, then a duct or pipe can be run over the panel, so long as it is more than 6 feet above the top of the panel, and so long as you install a drip shield.

 
Structural ceiling is the bottom of joists or trusses above you on the level of the building you are on. A foreign system can run in the space above the structural ceiling even if the equipment requiring dedicated space is right up to the structural ceiling. Might not be a good idea design wise but is NEC compliant.

.....

Exception that follows allows suspended ceilings with removable panels in said zone but they are not part of the structural ceiling, so the dedicated space extends past a suspended ceiling.

Concerning the definition of a "structural ceiling", suppose you have a 8 ft from the finished floor to the bottom of the joists for the next higher storey, and the joists are 2 ft tall. On top of the joists, is the corrugated steel decking and slab for the next floor. The space between the joists is open.

Where is the structural ceiling in this room? Is it 8 ft above the floor, or 10 ft above the floor? Could you run foreign systems through the open joists, above equipment that requires dedicated space?

If the joists are open, I'd consider the decking to be the structural ceiling. If there is a drywall ceiling below the joists, directly attached to the bottom of the joists, I'd consider that drywall to be the structural ceiling
 
Concerning the definition of a "structural ceiling", suppose you have a 8 ft from the finished floor to the bottom of the joists for the next higher storey, and the joists are 2 ft tall. On top of the joists, is the corrugated steel decking and slab for the next floor. The space between the joists is open.

Where is the structural ceiling in this room? Is it 8 ft above the floor, or 10 ft above the floor? Could you run foreign systems through the open joists, above equipment that requires dedicated space?

If the joists are open, I'd consider the decking to be the structural ceiling. If there is a drywall ceiling below the joists, directly attached to the bottom of the joists, I'd consider that drywall to be the structural ceiling
Structural ceiling is 8 feet above the floor IMO. Dedicated space on the next floor would start at floor level on that next floor - you have two feet of space between floors that is not dedicated space should there be electrical equipment directly above on the next floor, but sure would be nice if you have a feed through situatiuon that they leave you room to do so.
 
OK, kwired. I see how we are appearing to disagree with each other. But we are not. This is one of those famous arguments that goes like this:
Person 1 says, "The grass is green."
Person 2 says, "No, you are wrong. The sky is blue."


I like that argument! :p

just to add on to my original questions:

1) Suppose you had ductwork 2 feet above the panel. that's obviously a violation. Would encasing the ductwork in sheetrock help, or are you still in violation?
2) What if you had a soffit or gypsum board ceiling 2 feet above the panel? is this a violation? the code says the ceiling, if less than 6 feet above, has to be a dropped or suspended ceiling. so if it's a solid ceiling, is it a violation?
 
I like that argument! :p

just to add on to my original questions:

1) Suppose you had ductwork 2 feet above the panel. that's obviously a violation. Would encasing the ductwork in sheetrock help, or are you still in violation?
2) What if you had a soffit or gypsum board ceiling 2 feet above the panel? is this a violation? the code says the ceiling, if less than 6 feet above, has to be a dropped or suspended ceiling. so if it's a solid ceiling, is it a violation?
1) Encasing it will not help, since the soffit is not a structural ceiling. It occupies space that might later be needed for electrical purposes.
2) If it is a dropped or suspended ceiling, the space above it is still available for electrical purposes. If it is a solid ceiling but not the structural ceiling, the space is not available, but there is space there. No good. If the structural ceiling is less than 6' above the panel, does that mean the panel cannot be there? I think not.
 
OK, kwired. I see how we are appearing to disagree with each other. But we are not. This is one of those famous arguments that goes like this:
Person 1 says, "The grass is green."
Person 2 says, "No, you are wrong. The sky is blue."

So let me revise my earlier post to clarify (revised wording is in bold, red text):

  • If the structural ceiling is less than 6 feet above the top of the panel, then no ducts or pipes can be between the top of the panel and the bottom of the structural ceiling.
  • If the structural ceiling is more than 6 feet above the top of the panel, then a duct or pipe can be run over the panel, so long as it is more than 6 feet above the top of the panel, and so long as you install a drip shield.


You are a better man than me. I couldn't even find where he said anything you didn't. What you said made perfect sense and what he said was a more convoluted and wordy example of the same thing. In this area where our inspectors are ridiculously over the top tough, they for some reason allow a building to install a 1 hour rated ceiling under the foreign system and determine that it meets code. I guess they have decided that a 1 hour ceiling is a structural ceiling. The fact is, I haven't found a valid legal description of "structural ceiling" in either the NEC of the Building code, so...........
 
1) Encasing it will not help, since the soffit is not a structural ceiling. It occupies space that might later be needed for electrical purposes.
2) If it is a dropped or suspended ceiling, the space above it is still available for electrical purposes. If it is a solid ceiling but not the structural ceiling, the space is not available, but there is space there. No good. If the structural ceiling is less than 6' above the panel, does that mean the panel cannot be there? I think not.


I posted a posit below, and not to be argumentative, because I believe it is not a structural ceiling, but can you provide me with a legal building definition of a structural ceiling? What about a mezzanine is that a structural ceiling? What if the mezzanine is only 2 feet wide?
 
1) Encasing it will not help, since the soffit is not a structural ceiling. It occupies space that might later be needed for electrical purposes.
2) If it is a dropped or suspended ceiling, the space above it is still available for electrical purposes. If it is a solid ceiling but not the structural ceiling, the space is not available, but there is space there. No good. If the structural ceiling is less than 6' above the panel, does that mean the panel cannot be there? I think not.

I agree with your answer for my 2nd question... however, when is that ever seen? you will always see a solid ceiling a few feet above the panel... never will you see it above the 6 foot requirement.
 
The way you worded this has me confused over what you intended to say. So let me say it this way:
  • If the structural ceiling is less than 6 feet above the top of the panel, then no ducts or pipes can be above the panel.
  • If the structural ceiling is more than 6 feet above the top of the panel, then a duct or pipe can be run over the panel, so long as it is more than 6 feet above the top of the panel, and so long as you install a drip shield.

Is that what you were trying to say?


You are a better man than me. I couldn't even find where he said anything you didn't. What you said made perfect sense and what he said was a more convoluted and wordy example of the same thing. In this area where our inspectors are ridiculously over the top tough, they for some reason allow a building to install a 1 hour rated ceiling under the foreign system and determine that it meets code. I guess they have decided that a 1 hour ceiling is a structural ceiling. The fact is, I haven't found a valid legal description of "structural ceiling" in either the NEC of the Building code, so...........
The part I bolded in above quote is what I disagreed with and I did not (intend to, if that is how it was interpreted)say the same thing as that says.

If the structural ceiling is less than 6 feet above the top of the panel, then ducts or pipes can be above the panel, if they are also above the structural ceiling.

You maybe have a reasonable argument on what is a structural ceiling though. I think most will agree though if a part of the structure would possibly collapse if the item in question were to be disturbed or removed then it is a structural member.

A suspended ceiling is only designed to hold itself and maybe some accessories, not to reinforce other portions of the structure in any way.

Been in remodels in old houses where plaster ceilings are in bad shape, and they maybe just drop a "hard ceiling" a little lower maybe some 2x4 or 2x6 members spanning across the room and cover with new drywall. That I would not call a structural ceiling - it's only function is to hold the ceiling finish up and not to provide any structural support or reinforcement.
 
If the structural ceiling is less than 6 feet above the top of the panel, then ducts or pipes can be above the panel, if they are also above the structural ceiling.

And I just felt that it is splitting hairs and for purposes of this discussion his wording spelled it out just fine. One could just as well argue that the are not above the panel, the are above the ceiling. And I don't mean offence, I just agree with him.
 