Does the article 110.26(F)(1) pertain to foreign systems inside a wall cavity. I have a house with a recessed panel that opens out to a kitchen. It shares a wall with a bathroom. The original installers put the shower head and other assorted plumbing in this same bay as the panel. Is this legal. I thought at first it was, but I'm having seconded thoughts.....would really like to make sure thanks.
 
Re: dedicated electrical space

(F) Dedicated Equipment Space. All switchboards, panelboards,
distribution boards, and motor control centers shall be
located in dedicated spaces and protected from damage.

A panel board in whose bath, kitchen?
 
Re: dedicated electrical space

Ryan, can you cite a reference?

The nature of 110.26 as laid out in it's opening statement is for adequate space to work on equipment, not space to get other concealed systems out of the same bay.

I think it's compliant.

I would never have conceived of such an installation! :D
 
Re: dedicated electrical space

110.26(F)(1), covers the space the "footprint" of the equipment occupies. the "bay" of the wall is the "occupied" space, therefore if the pipes are in the dedicated space, they are not permitted.
Ryan has a much better way of saying this ;)
 
Re: dedicated electrical space

it seems to me that is there is no pipe above and 30 iches of space why would it not be code compliant. Ypou and I mite note ever put the pipe this close but its there and what does it hurt? iT certainly does not interefere with the intent is the space requirement which is to allow for worrking space.
 
Re: dedicated electrical space

it seems to me that is there is no pipe above and 30 iches of space why would it not be code compliant. You and I mite note ever put the pipe this close but its there and what does it hurt? iT certainly does not interfere with the intent is the space requirement which is to allow for working space.
 
Re: dedicated electrical space

Not only working space, but also the pathway for present and future circuit runs.
 
Re: dedicated electrical space

Ryan, Pierre,
This section needs some work as it actually prohibits the installation of recessed panles.
The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation.
While the section goes on to prohibit some specific items the rule is general in nature. It applies to things other than those specified, as shown by the exception for suspended ceilings. The top plate of the wall is not the structural ceiling and it is in the required dedicated space making it impossible to install a recessed panel.
Don
 
Re: dedicated electrical space

Originally posted by don_resqcapt19:
Ryan, Pierre,

The top plate of the wall is not the structural ceiling and it is in the required dedicated space making it impossible to install a recessed panel.
Don
I was thinking about that last night actually, although I was thinking about the bottom plate of the wall (same difference).

George, Stew: 110.26(F) is the section I am refering to.
 
Re: dedicated electrical space

It is near time to celebrate the birth of the one who saves us from the devil, so I am taking a chance playing the "devil's advocate." But here I go.
</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">110.26(A)(1) tells me that for an enclosed panel (like the one under discussion), the working space begins at the front of the panel, not the back.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">110.26(A)(1)(a) tells me that I don't need working space on the sides of this panel.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">From these two, I infer that the pipes are not within the required working space.
</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">110.26(F)(1)(a) tells me that the space directly above and below the panel (but not necessarily to the side of the panel), from floor to ceiling (including within the wall, since the panel is recessed), cannot have pipes.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">From this I infer that the water pipe for the shower head can run vertically, from floor to the height of the shower head, within the wall cavity and to the side of the panel. The fact that this may take away room that you might want to use for future conduits means nothing.

I conclude that this is code compliant.

Can I resign from my advocacy job and return to being a "believer" now? ;)
 
Re: dedicated electrical space

Originally posted by charlie b:

Can I resign from my advocacy job and return to being a "believer" now? ;)
Yes you may. ;)

Roger
 
Re: dedicated electrical space

I believe the required working space and the dedicated space above panels are refering to two different items. One allows a safe working space, and the other prevents foreign pipes or other foreign systems from intruding above the space occupied by panels or switchgear. IMHO, Don, and Ryan are correct about the top plate issue with recess panels. Either a code change proposal to fix this wording is needed, or we make a willful and wonton violation every time we install a flush panel in a standard residential wall space. Merry Christmas everyone.
 
Re: dedicated electrical space

Originally posted by macmikeman:
Either a code change proposal to fix this wording is needed, or we make a willful and wonton violation every time we install a flush panel in a standard residential wall space.
I vote for the latter. :p We gotta get away with something every once in a while.
 
Re: dedicated electrical space

From this I infer that the water pipe for the shower head can run vertically, from floor to the height of the shower head, within the wall cavity and to the side of the panel. The fact that this may take away room that you might want to use for future conduits means nothing.
If I'm reading this correctly, you're saying that the pipe is not running above the panel but next to it? If this is what you meant than I would agree with Charlie's assessment, however typical stud spaces are 14 1/2" wide and so are the panels. Sounds like the pipe won't fit next to it within the same stud space.
 
Re: dedicated electrical space

Just when you think you got certain parts of the code down....


We all know that for more time than we can think, that panels have been installed in the recess of walls. Now, we finally see that the wording, if taken how it is written tells us this is not permitted. We also know this probably was not the intent, but intent is not what is necessarily written.
For now, we are mostly violating this section, so I do see a small code change for clarification.
To tell electricians they cannot do this would be the same as asking for a beating!!!
 
Re: dedicated electrical space

Actually 90.1 (A) through (D)
90.7, Examination of Equipment for Safety,
90.8 (A) & (B),
110.2 Approval
110.3, Examination, Identification, Installation, and Use of Equipment., especially 110.3(A)(1), (2), (7) and (8); and 110.3(B).
110.11 Deteriorating Agents. Unless identified for use in the operating environment, no conductors or equipment shall be located in damp or wet locations..."
110.12,
110.26 (F)(1)
300.4(D)&(E)
300.6 and specifically (D), i.e. shower wall on opposite side of enclosure is "frequently washed".
300.7 regards to RH/Condensation within the wall cavity (A),
and
300.8 Installation of Conductors with Other Systems. Raceways or cable trays containing electrical conductors shall not contain any pipe, tube, or equal for steam, water, air, gas, drainage or any service other than electrical.

Your location is at minimum a damp one, likely potentially a wet one, adjust your thinking accordingly. (through's of the plumbing on the other side of the shower wall/tile no longer continuous regards the concrete/tile, etc. exception).
 
Re: dedicated electrical space

pierre, I am just going to tell the carpenter that he has to cut the sole and top plate out. That way I only have to see the first half second or so of the beating.
 
Re: dedicated electrical space

Originally posted by lesliek:
Your location is at minimum a damp one, likely potentially a wet one, adjust your thinking accordingly.
Just how do you figure it is a damp location?
 