Dedicated Equipment Space 110.26(E)(1)

vitality555

New User
Location
California
Occupation
EE
Does dedicated equipment space refer only to switchboards, switchgear, panelboards, and motor control centers or to all electrical equipment such as:
* disconnects, control panels, analyzers.
 
Does dedicated equipment space refer only to switchboards, switchgear, panelboards, and motor control centers or to all electrical equipment such as:
* disconnects, control panels, analyzers.
I've had this discussion with a few inspectors. Some of them require the working space requirement on A/C disconnects if they happen to be behind the A/C. I asked them if this was a requirement for a switch and they said no. I replaced the non-fusible disconnect with a 2-pole 40A switch and left it in the same place. Then it passed inspection. I think my point was made although it cost me a little more money. LOL
 
I've had this discussion with a few inspectors. Some of them require the working space requirement on A/C disconnects if they happen to be behind the A/C. I asked them if this was a requirement for a switch and they said no. I replaced the non-fusible disconnect with a 2-pole 40A switch and left it in the same place. Then it passed inspection. I think my point was made although it cost me a little more money. LOL
Yes working space is different. The OP asked about dedicated equipment space.
 
I see. In reference to my post, would you require a non-fusible disconnect to have working space? Would you require a 2 pole switch have working space?
I would not, but I wouldn't require it in front of a fused switch either. There is no reason to examine, test etc. a fused switch while energized that can't be performed deenergized.
 
I see. In reference to my post, would you require a non-fusible disconnect to have working space? Would you require a 2 pole switch have working space?
I recommend always planning to have working space, on any equipment exceeding the voltage and/or ampacity of simple light switches and receptacles. I.e. those are devices where we know are acceptable to put them on the back of a counter, or inside a cabinet.

The proper way to build an A/C setup, is to mount the disconnect off to the side of the unit, so you can easily get to it and access it. The user shouldn't have to reach/climb over the A/C, or squeeze behind it, to use the disconnect.
 
I recommend always planning to have working space, on any equipment exceeding the voltage and/or ampacity of simple light switches and receptacles. I.e. those are devices where we know are acceptable to put them on the back of a counter, or inside a cabinet.

The proper way to build an A/C setup, is to mount the disconnect off to the side of the unit, so you can easily get to it and access it. The user shouldn't have to reach/climb over the A/C, or squeeze behind it, to use the disconnect.
I agree 100%. But when A/C contractors brig their own concrete pads and set them right in front of your disconnect, you don't really have that choice. I've trimmed out a lot of houses where the A/C contractor is behind schedule and we just mounted the disconnect and provided a whip. This is where most of the issues that I'm referring to are coming from.
 
I agree 100%. But when A/C contractors brig their own concrete pads and set them right in front of your disconnect, you don't really have that choice. I've trimmed out a lot of houses where the A/C contractor is behind schedule and we just mounted the disconnect and provided a whip. This is where most of the issues that I'm referring to are coming from.
This seems to be one of the most blatantly violated requirements I see. AFA it needing servicing or testing while energized, EVEN IF the breaker is turned off, the line side is to be presumed live until confirmed to be deenergized by testing (live work). Working space is required.
The proper way to build an A/C setup, is to mount the disconnect off to the side of the unit, so you can easily get to it and access it. The user shouldn't have to reach/climb over the A/C, or squeeze behind it, to use the disconnect.
The hazard can be deadly as most existing installations will not have GFCI and if you have to reach over and potentially "lean on" the AC unit to de-energize a shorted out unit. And the TIA is still there for some new installations, exempting GFCI.
 
I would not, but I wouldn't require it in front of a fused switch either. There is no reason to examine, test etc. a fused switch while energized that can't be performed deenergized.
The very first place I would start if I am troubleshooting AC equipment. If there is voltage on the load side, then I start taking off the equipment cover.
 
This seems to be one of the most blatantly violated requirements I see. AFA it needing servicing or testing while energized, EVEN IF the breaker is turned off, the line side is to be presumed live until confirmed to be deenergized by testing (live work). Working space is required.

The hazard can be deadly as most existing installations will not have GFCI and if you have to reach over and potentially "lean on" the AC unit to de-energize a shorted out unit. And the TIA is still there for some new installations, exempting GFCI.

If you turned down the job as an inspector and I replaced the non-fusible disconnect with a 2 pole switch, would this be considered a violation?
 
The very first place I would start if I am troubleshooting AC equipment. If there is voltage on the load side, then I start taking off the equipment cover.
But you shouldn't. You should turn the disconnect off and measure the fuses for continuity. Otherwise, as discussed here before we should be suited up to check for voltage. I must admit I don't. We can go down a rabbit hole of making things safe, or use common sense. Given the wording of 110.26, all receptacle and switches also require working clearance. I am not arguing with you or disputing what you are saying, I am just of the opinion that the requirements are a little over the top.
 
But you shouldn't. You should turn the disconnect off and measure the fuses for continuity. Otherwise, as discussed here before we should be suited up to check for voltage. I must admit I don't. We can go down a rabbit hole of making things safe, or use common sense. Given the wording of 110.26, all receptacle and switches also require working clearance. I am not arguing with you or disputing what you are saying, I am just of the opinion that the requirements are a little over the top.
Whether that should or should not be done does not matter. It is likely that it will be done and that triggers the application of 110.26(A).
As far as air conditioning equipment, CMP 11 took away any debate on this issue by adding "Disconnecting means shall meet the working space requirements of 110.26(A)." to the language in 440.14 in the 2023 code.
 
Whether that should or should not be done does not matter. It is likely that it will be done and that triggers the application of 110.26(A).
As far as air conditioning equipment, CMP 11 took away any debate on this issue by adding "Disconnecting means shall meet the working space requirements of 110.26(A)." to the language in 440.14 in the 2023 code.
So, what about clearance in front of a receptacle?
 
So, what about clearance in front of a receptacle?
Yes, every kitchen countertop receptacle is a violation:p, but CMP 1 refuses to correct unreasonable code language. The application of 110.26(A) should be limited in scope like 110.26(E) is. Maybe not the same list, but a limiting list. There have been multiple proposals over time to make changes to 110.26(A) but they have all be rejected.
 
Last edited:
Yes, ever kitchen countertop receptacle is a violation:p, but CMP 1 refuses to correct unreasonable code language. The application of 110.26(A) should be limited in scope like 110.26(E) is. Maybe not the same list, but a limiting list. There have been multiple proposals over time to make changes to 110.26(A) but they have all be rejected.
Yeah just another example of how clueless the CMP is. :mad:
 