Dedicated Equipment Space (110.26(E)) below a meter/main

Status
Not open for further replies.

marmathsen

Senior Member
Location
Seattle, Washington ...ish
Occupation
Electrical Contractor
Would a meter/main be considered a Switchboard, Switchgear, or Panelboard thus subject to the requirements of 110.26(E)? As a residential electrician, I struggle to parse the difference between them the three as their defined in 100.

To be clear I'm specifically talking about a 320A meter/main with (2) 200A disconnects in separate compartments. Eaton U4042MCC
https://rexel-cdn.com/products/4.pdf?i=7E75AA73-D8C5-4CB3-BDE5-6FA4EFBA7EEB

Thanks in advance
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IMO yes, it meets the Article 100 definition of a panelboard.

Panelboard. A single panel or group of panel units designed for assembly in the form of a single panel, including buses and automatic overcurrent devices, and equipped with or without switches for the control of light, heat, or power circuits; designed to be placed in a cabinet or cutout box placed in or against a wall, partition, or other support; and accessible only from the front.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Not relevant to the OP, but how about a meter/main with just one OCPD? Seems like it would not meet the definition of a panelboard.

Cheers, Wayne
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
What if it's only the meter enclosure?
If it's just the meter socket, I'd say it doesn't need the dedicated equipment space.

But he said 'meter/main' so that is service equipment.

Note that 'service equipment' was added in 2023. So if you're still on the 2020, then you can argue that a meter/main with main breaker only is exempt, whereas a meter/main with a panelboard distribution is not exempt. Which makes some sense, since the main-breaker-only box doesn't need as many circuits brought to it.
 

kwired

Electron manager
Location
NE Nebraska
Not relevant to the OP, but how about a meter/main with just one OCPD? Seems like it would not meet the definition of a panelboard.

Cheers, Wayne
I think it does meet the definition. And so does a single enclosed breaker assembly. Single meter only does not meet the definition. That don't mean some POCO's won't have their own clearance rules around these though.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Depends on how much weight you put on the plural-ness of "automatic overcurrent devices."

Are fused disconnects and enclosed (single) breakers listed to UL 67, or is there a different listing standard?

Cheers, Wayne
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Depends on how much weight you put on the plural-ness of "automatic overcurrent devices."

Are fused disconnects and enclosed (single) breakers listed to UL 67, or is there a different listing standard?

Cheers, Wayne
The requirements for both of those are found in UL 67.
 