E Electrobe Member Jun 15, 2016 #1 Is the dedicated Equipment Space of 110.26(E) required above Industrial Control Panels? I have an installation where there are water lines and a natural gas line above a industrial control panel with minimal space to route the electrical. Thanks
Is the dedicated Equipment Space of 110.26(E) required above Industrial Control Panels? I have an installation where there are water lines and a natural gas line above a industrial control panel with minimal space to route the electrical. Thanks
dkidd Senior Member Location here Occupation PE Jun 15, 2016 #2 Not required, but a good idea. 110.26 lists the equipment covered by it.
E Electrobe Member Jun 15, 2016 #3 dkidd said: Not required, but a good idea. 110.26 lists the equipment covered by it. Click to expand... That's what I thought but was hoping it was required somewhere else in the code. Definitely a good idea! Thanks