Is dedicated space above equipment over 1000V required by the NEC? If so, please provide an NEC reference. Thanks.
No Code requirement.Is dedicated space above equipment over 1000V required by the NEC? If so, please provide an NEC reference. Thanks.
110.32 says nothing about dedicated space above the equipment.110.32
No Code requirement.
Thank you both.I agree with David. The dedicated space requirement is in 110.26(E). That article applies to 1000 volts or under. There is no similar requirement for over 1000 volts.