Nelson electric

Christian
Location
Sacramento, ca
Occupation
Electrician
A dedicated equipment transformer has 480 volt line voltage with 120/220 secondary voltage.
Phase 1 reads 118
Phase 2 reads 131
Phase 3 reads 118
Why would the middle phase read 131?
 
unbalanced loads

unbalanced loads

What is the current on them?
How far is the feed.

You can have a large single phase load on a-c phase and no load on b phase. If the feeders were too small this is how voltage drop would show up.
 
A dedicated equipment transformer has 480 volt line voltage with 120/220 secondary voltage.
Phase 1 reads 118
Phase 2 reads 131
Phase 3 reads 118
Why would the middle phase read 131?

As Dave stated the secondary voltage would be either 240/120 or 208Y/120. If it's 3Ø, 4W Delta your secondary voltages should be 120-208-120 to ground.
 