I believe these NEC sections apply.
220.18 Maximum Loads.
The total load shall not exceed
the rating of the branch circuit, and it shall not exceed the
maximum loads specified in 220.18(A) through (C) under
the conditions specified therein.
(B) Inductive and LED Lighting Loads.
For circuits sup-
plying lighting units that have ballasts, transformers, au-
totransformers, or LED drivers, the calculated load shall be
based on the total ampere ratings of such units and not on
the total watts of the lamps
210.19(A)(1) General.
Branch-circuit conductors shall have an am-
pacity not less than the maximum load to be served. Con-
ductors shall be sized to carry not less than the larger of
210.19(A)(1)(a) or (b).
(a) Where a branch circuit supplies continuous loads
or any combination of continuous and noncontinuous loads,
the minimum branch-circuit conductor size shall have an
allowable ampacity not less than the noncontinuous load
plus 125 percent of the continuous load.
(b) The minimum branch-circuit conductor size shall
have an allowable ampacity not less than the maximum
load to be served after the application of any adjustment or
correction factors.
410.6 Listing Required.
All luminaires, lampholders, and
retrofit kits shall be listed