Dedicated receptacle for counter microwave required to be GFCI protected?

Status
Not open for further replies.

Rod T

New member
Location
Fresno, CA
Can't find an answer to this scenario so thought I'd post to see what others think. I have a dedicated single receptacle and dedicated circuit for a microwave that will sit on the kitchen counter. It will serve only the microwave and not the counter as 2008 NEC 210.8 (A)(6) states must be GFCI protected. Am I correct not needing to GFCI protect this receptacle as it's purpose is not a SABC?
 
When the present homeowners move out and take the microwave with them, or when the microwave breaks down and they decide not to replace it, that receptacle becomes available to power other appliances that might be placed on the countertop. My opinion is that that circuit is a SABC, and that it must therefore be a 20 amp and be GFCI protected.
 
Agree that it has to be GFCI but does it have to be called SABC? i guess if it is not SABC then it can be 15A instead of 20A?
 