2008 NEC - 210.11(C)(3) requires a 20A branch circuit in the bathroom to supply only receptacles. The exception says: where the 20A circuit supplies a single bathroom, outlets for other equip within the same bathroom shall be permitted in accordance with 210.23(A)(1) and (A)(2)
210.23(A) says a 15A or 20A branch circuit shall be permitted to supply lighting units or other utilization equip, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2) The exception says: ...bathroom branch circuits required in a dwelling unit shall supply only the receptacle outlets.
These two codes seem to contridict one another. One says a dedicated 20A circuit can supply all outlets (lights, exhaust fan, etc.) and receptacles from the same dedicated circuit. The other says only receptacles can be on the 20A circuit and not the lights, fan, etc. Which is it? Can I wire a new bathroom with one 20A circuit to include the receptacles, lighting, fan, ect. or not?
210.23(A) says a 15A or 20A branch circuit shall be permitted to supply lighting units or other utilization equip, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2) The exception says: ...bathroom branch circuits required in a dwelling unit shall supply only the receptacle outlets.
These two codes seem to contridict one another. One says a dedicated 20A circuit can supply all outlets (lights, exhaust fan, etc.) and receptacles from the same dedicated circuit. The other says only receptacles can be on the 20A circuit and not the lights, fan, etc. Which is it? Can I wire a new bathroom with one 20A circuit to include the receptacles, lighting, fan, ect. or not?