110.26(E) requires dedicated space for SWBDs, SWGR, Panelboards and MCC's.
I am of the belief, that the equipment that needs this dedicated space would be listed as one of these pieces of equipment.
A battery cabinet for a UPS that has an output breaker mounted in it (listed as IT equipment), does not make it a panelboard needing dedicated space.
Do you disagree?
I am of the belief, that the equipment that needs this dedicated space would be listed as one of these pieces of equipment.
A battery cabinet for a UPS that has an output breaker mounted in it (listed as IT equipment), does not make it a panelboard needing dedicated space.
Do you disagree?