dnunez
Member
- Location
- Scottsdale, AZ
We are installing 200A 1PH 240V sub panels in a 9 story condo Hi-rise(Arizona). Each unit has a sub-panel. The panels are flush mounted in a 6" metal stud wall that goes from floor to concrete structure above. (Approx 11')
There will be a Hardlid framed ceiling at 9' AFF but does not pass thru the wall. My inspector, per NEC 110-26(F)(1), will not allow any ducting, Sprinkler, or plumbing pipe to pass above these subpanels in the above ceiling space. After thoroughly reading this code I cannot find any way around either moving the panels or clearing the space above the panels in the framed walls to meet this code. Any thoughts or suggestions would be greatly apprieciated.
There will be a Hardlid framed ceiling at 9' AFF but does not pass thru the wall. My inspector, per NEC 110-26(F)(1), will not allow any ducting, Sprinkler, or plumbing pipe to pass above these subpanels in the above ceiling space. After thoroughly reading this code I cannot find any way around either moving the panels or clearing the space above the panels in the framed walls to meet this code. Any thoughts or suggestions would be greatly apprieciated.