I am currently retired (IBEW Local 3, AFSCME Local 444) and was asked to following question by my friend:
The panel is a Square D SU3040D400CB, with two 200 amp breakers. (Large house and woodworking shop with high demand, both under construction. I have not seen his load calcs.)
His electrician pulled 350 Kcmil AL service-entrance conductors, I would guess based on a calculation of 83 percent of the meter's continuous rating of 320 amps. The AHJ tagged the service-entrance conductors as too small, no further explanation. (I suspect he is defining the size of the service as 400 amp).
What is the correct definition of the service and size of the service-entrance conductors. I have seen conflicting responses on the forum.
Thanks all.
The panel is a Square D SU3040D400CB, with two 200 amp breakers. (Large house and woodworking shop with high demand, both under construction. I have not seen his load calcs.)
His electrician pulled 350 Kcmil AL service-entrance conductors, I would guess based on a calculation of 83 percent of the meter's continuous rating of 320 amps. The AHJ tagged the service-entrance conductors as too small, no further explanation. (I suspect he is defining the size of the service as 400 amp).