hillbilly1
Senior Member
- Location
- North Georgia mountains
- Occupation
- Owner/electrical contractor
One of my guys from a previous employer called me today saying he was having issues with a single phase step down transformer. He said the primary voltage goes to zero when the transformer is connected (1kva). The transformer is mounted to the side of the panel, and has another just like it mounted on the other side of the panel. Both are doing exactly the same thing, and are on separate circuits. Breaker is not tripping. I had him move it the other phases, same thing. Voltage from the panel busses good phase to phase, phase to neutral, phase to ground, with no voltage neutral to ground. He has no other spares to try. It would be really odd that he has two bad breakers, everything is new including the panel. Only two other loads in the panel, two 90 amp three poles for two three phase EV truck chargers, and he says those are working. Forgot to have him do a fop test on the breaker, but he said the buss voltage remained good with that transformer connected, just the breaker output went to zero.
The customer supplied the equipment, and is a well known importer of Chinese goods. I’m wondering it they may be counterfeit breakers?
The customer supplied the equipment, and is a well known importer of Chinese goods. I’m wondering it they may be counterfeit breakers?