Throughout the NEC, "total connected load" and "demand load" represent two allowed calculation methods for what is really our system's "real power". Apply the power factor(s) and you get the system's "apparent power".
NEC 220.87 uses the phrase "[actual] maximum demand data" for determining existing loads. Typically when applying this section, I see that utility maximum demand data is given in kW rather than VA. Is this a measure of the system's real power, and thus we have to apply power factor(s) to calculate apparent load?
NEC 220.87 uses the phrase "[actual] maximum demand data" for determining existing loads. Typically when applying this section, I see that utility maximum demand data is given in kW rather than VA. Is this a measure of the system's real power, and thus we have to apply power factor(s) to calculate apparent load?